| GordonCooks | "Rheem w HSI" , posted Tue 28 Oct 12:26  
Hello and thanks in advance for any advice. I have a Rheem gas furnace approx 1o years old. There seems to be what I would consider an abnormal delay in getting the furnace to fire and occasionally - no fire at all.
Typically -Programmable stat calls for heat -Vent motor starts (not sure if this is supposed to happen before/after pilot goes on) -Ignitor glows -Gas valve clicks -Furnace ignites
This occurred within a few minutes. Occasionally, the stat calls for heat and the ignitor glows for what could be 10-20 minutes to hours(no fan on either). Not sure if it's the S89G module controlling everything or something hanging up in the circuit. If I reset everything - the problem subsides for a while.
| | Replies:
|
| djgilbert | "Re(1):Rheem w HSI" , posted Tue 28 Oct 19:52  
It sounds like the burners need to be removed and cleaned or replaced.
Don
|
| | GordonCooks | "Re(2):Rheem w HSI" , posted Wed 29 Oct 08:09  
Just pull out the tube assembly for the pilot gas bar? Or the main burners? I do remember cleaning the pilot gas orifice tube last year figuring maybe the gas was not reaching the pilot but I will revisit this again. Thank you.
If you mean the main burner assembly - can you give me a little more info on how this is causing the problem?
|
| | Houston204 
| "Re(2):Rheem w HSI" , posted Tue 28 Oct 22:14  
Faulty PC board.
"Tip of the Day" Remember to remove power first.
|
| | GordonCooks | "Re(3):Rheem w HSI" , posted Wed 29 Oct 08:12  
PC Board meaning replace the module? Thanks
|
|
|
|  |
|