"furnace" , posted Tue 28 Oct 22:29user profileedit/delete messagepost reply


my furnace will put good heat out when it first kicks on. after that the flame goes out and runs twice as long with no flame cooling the house back off.it will shut off then 5 minutes later kicks back on and repeats that cycle.any help is greatly appreciated

 


Replies:

Schock Therapy

75.157.133.30

"Re(1):furnace" , posted Wed 29 Oct 19:56user profileedit/delete messagepost reply


If the thermostat gets up to temp and cycles the burners off, the fan will continue to run until the fan control thermostat opens. This is to cool the heat exchanger down. There may be a problem with the fan control. It could also be that the thermostat is being influenced by warm air from a nearby supply air vent. Short-cycling like that is also a problem caused by the furnace being over sized for the space.

It's only a shock if your not expecting it!

 

 

moto134

76.235.74.200

"Re(2):furnace" , posted Wed 29 Oct 21:03user profileedit/delete messagepost reply


the thermostat doesnt get up to temp.i have already replaced the fan control tstat i think. doesnt it just touch the heat exchanger with one wire on both ends. and there are no vents near the thermostat.i appreciate you taking your time for me!!!

 

learner

70.73.177.71

"Re(1):furnace" , posted Wed 29 Oct 01:35user profileedit/delete messagepost reply


Hi,
Is the filter clean?