RHEEM RGVH-07EAUER Heat Almost works - http://www.hvacmechanic.com/ Forums
Original message
| acedagger 
| "RHEEM RGVH-07EAUER Heat Almost works" , posted Wed 29 Oct 22:35  
RHeem Model RGVH-07EAUER SN (CY50302?) F1194 6448 Control board Model 1012-920A Additional number on control board 62-24084-02
1. When Thermostat set to cool -works - unit cycles correctly 2. When Thermostat set to off and fan to on - unit blows 3. When Thermostat set(or turned) to heat - blower shuts off. 3a. Induced draft blower starts - yes 3b. 30sec Prepurge - yes 3c. Igniter warms up 34sec warmup +9for ignition - yes 3d. Main burner lights 3e. Main burner continues to burn 3f. After 20 seconds I hear a click but no blower motor and I can't even manually override because it won't come on even if i set the fan to ON at the thermostat (if it is set to heat) I am having a hard time finding out which wire triggers the fan from the heat mode? can anybody give me a terminal to test for power?
| | Replies:
|
| Silvertop 
| "Re(1):RHEEM RGVH-07EAUER Heat Almost works" , posted Fri 31 Oct 00:52  
Green is the fan and red is your hot at the thermostat if the tech wired it by color code.
One step at a time
|
| | hollywood | "Re(2):RHEEM RGVH-07EAUER Heat Almost works" , posted Fri 31 Oct 13:52  
The board controls the blower in heat mode.If the blower is not coming on in heat the board is bad.
|
|
|
|  |
|