"coleman" , posted Thu 30 Oct 19:45user profileedit/delete messagepost reply


i need help with this. a coleman heatpump unit installed in a manufactured home has a brown wire connected to the 'E' terminal in the t-stat. However I found that it is not connected to anything in the air handler. Therefore the heat strpis do not come on neither does the aux. heat. Where should this "E" be connected to the blower relay or to the heat sequencer? Or could there be another reason the strips don't energize? The high voltage is there and the meter reads 18vac on the coils of the blower relay and at the sequencer. I WOULD APPRECIATE any help. thanx

learn something from everyone

 


Replies:

Houston204



98.196.66.53

"Re(1):coleman" , posted Fri 31 Oct 00:16user profileedit/delete messagepost reply


I recommend using www.photobucket.com to post some pictures of your fancoil wiring.

"Tip of the Day" Remember to remove power first.