proper sizing of furnace - http://www.hvacmechanic.com/ Forums
| Original message
| Replies:
|
| ampulman | "Re(1):proper sizing of furnace" , posted Fri 31 Oct 15:33  
a 20 year old furnace with standing pilot and exhaust bonnet can run between 60 -70% efficient. This equates to a range of 48,000 - 56,000 BTU output.
The '60' furnace is a 2 stage variable speed unit, and has outputs of 31,200/48,000 BTUs; the '80' is a 2 stage unit with outpus of 41,600/64,000 BTUs. Usually, a difference of one size (in the same series) is relatively small.
Did any contractor do a heat calc? Considering the difference, one or both contractors are guessing. You can do one yourself. It will cost you $50. Go to HVAC-Calc.com.
Does your current furnace run (almost) constantly on the coldest day of the season. If not, then it's likely oversized.
AM
|
| | Freon | "Re(2):proper sizing of furnace" , posted Fri 31 Oct 15:46  
Simple question... on the coldest of winter nights, does your existing furnace run almost constantly AND keep you warm. If yes, then it's the perfect size (net BTU output of 48,000 - 56,000 BTU ). If it cycles on and off frequently, it may be too big. If you are cold, it may be too small.
|
|
|
|  |
|