Carrier Weathermaker 8000 won't stay on - http://www.hvacmechanic.com/ Forums


Original message

jvarick

72.49.212.45

"Carrier Weathermaker 8000 won't stay on" , posted Fri 31 Oct 15:58user profileedit/delete messagepost reply


My Daughter has a new house (to her)with a Carrier Weathermaker 8000 furnace. It seemed to be working fine until a few days ago. Now it will run for a while, then the burner will turn off, then when the burner kicks on again, the gas shuts off after about 3 seconds. It cycles through again, but everytime the burner kicks on, it only stays lit for a few seconds before the gas shuts off. After a few cycles of this, the furnace shuts down and doesn't start again until we turn it off and then back on. Could there be a sensor that is trying to measure whether or not the flame is on that is malfunctioning and shutting off the gas? Thanks for your time.

 


Replies:

learner

70.73.177.71

"Re(1):Carrier Weathermaker 8000 won't stay on" , posted Fri 31 Oct 23:01user profileedit/delete messagepost reply


Hi,Sounds like flame sensor is dirty. Clean it.

 

Houston204



98.196.66.53

"Re(1):Carrier Weathermaker 8000 won't stay on" , posted Fri 31 Oct 19:53user profileedit/delete messagepost reply


Clean your flame sensor with steel wool. (not sandpaper)


Avoid touching the ignitor.

"Tip of the Day" Remember to remove power first.

 

 

jvarick

72.49.212.45

"Re(2):Carrier Weathermaker 8000 won't stay on" , posted Mon 3 Nov 07:39user profileedit/delete messagepost reply


Cleaning the sensor appears to have worked. Thanks for the help.

 

 

jvarick

64.12.117.9

"Re(2):Carrier Weathermaker 8000 won't stay on" , posted Fri 31 Oct 19:58user profileedit/delete messagepost reply


I'll give it a try. Thanks for your quick response.