| techshawn | "Re(1):Aprilaire Carrier MPV Infinity" , posted Sun 2 Nov 16:23  
For Hum wiring, simple connect two wires to the 24v terminal on the board. One wire is from humidistat. one wire is from solenoid.
For the condensate pump, simply read the instruction. I've no idea about that.
I like fixing everything.
|
| | Houston204 
| "Re(2):Aprilaire Carrier MPV Infinity" , posted Mon 3 Nov 18:54  
Interrupt D (red) to the condenser with your condensate pump's float switch.
"Tip of the Day" Remember to remove power first.
|
| | chiefella | "Re(2):Aprilaire Carrier MPV Infinity" , posted Sun 2 Nov 18:12  
|
| | chiefella | "Re(3):Aprilaire Carrier MPV Infinity" , posted Mon 3 Nov 20:16  
Thanks. I have a follow up question.
The condening pump has 2 blue wires exiting the unit that require wiring. I understand you are recommending connecting one wire to the Interrupt D (red). Where should the other wire go?
|
| | Houston204 
| "Re(4):Aprilaire Carrier MPV Infinity" , posted Mon 3 Nov 23:14:  
Connect 1 blue wire to condenser D and the other to Furnace D. (Interrupting D to the condenser) Or, just cut the D wire to the condenser and connect one blue wire to each red. (The color of D should be verified at the furnace terminal block) This wire carries 24volt power to your condenser from the furnace. If your pump fails it will interrupt 24 volt power to the condenser, removing the water source.
"Tip of the Day" Remember to remove power first.
[this message was edited by Houston204 on Tue 4 Nov 21:12] |
| | hemikota804 | "Re(5):Aprilaire Carrier MPV Infinity" , posted Tue 4 Nov 23:54  
I dont know if you have already installed that thermostat but that wouldnt be my first choice actually my last. The best set up in my opinion is the new honeywell iaq thermostat with the IAQ interface module. The thermostat is touch screen you can operate your humidifier a dehumidification setting and a whole house ventilation control to bring in outside air if you have that set up. Best part is the thermostat only needs three wires. The interface module is a few more wires than that but wiring diagrams are very easy to follow.
|
| | Houston204 
| "Re(6):Aprilaire Carrier MPV Infinity" , posted Wed 5 Nov 01:13  
The Carrier Infinity control has better communication with Infinity equipment.
I would use a relay to avoid sending 48 volts to your 24 volt solenoid coil.
This WAV is an example.
"Tip of the Day" Remember to remove power first.
|
| | chiefella | "Re(7):Aprilaire Carrier MPV Infinity" , posted Thu 6 Nov 20:47  
Thanks for the diagram.
If I leave the humidstat connected, will it effect the the operation of the humidity function on the infinity thermostat? Also, if the humidistat remains connected, what setting should it be on? Can I wire the selenoid directly to the furnace circuit board bypassing the humidstat?
The current sensing relay I purchased only has 2 wires. Any suggestions on how I should wire it?
|
| | chiefella | "Re(7):Aprilaire Carrier MPV Infinity" , posted Thu 6 Nov 20:27  
|
|
|
|  |
|