Hello, I would like to replace my Lennox thermostat, P/N 36G6901, with a new Honeywell RTH 7600 but the wiring is different. I have a Lennox heat pump with electric emergency heat that is about 18 years old. (There is a Emergency Heat switch on the front of the old Lennox thermostat).
The wiring on my old thermostat is: R = BLACK V = BLUE F = GREEN M = RED L = BROWN A = WHITE Y = ORANGE (There is a RED jumper that goes into the old Termostat) X = YELLOW E = NO WIRE ON TERMINAL
The labels on the new thermostat are RC,R,O/B,Y,G,C,L,E,AUX. RC & R are jumped together.
Can you please tell me how to wire up the new thermostat. Honeywell is suggesting I contact my local HVAC person. Thanks!
Jim
| | Replies:
|
| Houston204 
| "Re(1):Honeywell RTH7600" , posted Tue 4 Nov 20:47:  
http://www.hvac-direct.com/pdf_files/service/8806.pdf
O/B = black (reversing valve) Rc & R = blue (24VAC) use supplied jumper G = green (fan) Y = red (compressor) L = brown (LED) tape off white (old thermister for heating, now obsolete) Aux & E = orange (electric heat strip) use a jumper C = yellow (common)
Your new stat must also be configured for heat pump operation. Option 170 = 7 190 = 0
"Tip of the Day" Remember to remove power first.
[this message was edited by Houston204 on Wed 5 Nov 19:46] |
| | jawerk | "Re(2):Honeywell RTH7600" , posted Tue 4 Nov 21:16  
Thanks for the information!