| learner | "Re(1):turn off single zone of multi-zone heat" , posted Thu 6 Nov 11:14  
Hi, Did you check the valve? It is possible it is stuck(jammed) open causing constant heating.
|
| learner | "Re(1):turn off single zone of multi-zone heat" , posted Thu 6 Nov 11:11  
Hi, It is possible solenoid valve is stuck open causing runaway heating.
|
| hemikota804 | "Re(1):turn off single zone of multi-zone heat" , posted Tue 4 Nov 23:33  
how many zones do you have. count up all the thermostats that you have and that is how many zones you have. If you turn the thermostat down below the room temp the zone should shut off. Is your system in runaway heat where you cant shut if off and it just keeps on running and running. let me know. Have you had anyone in the house working on the system they may have left the zone valves in the manual position instead of auto. My guess is you have a shorted thermostat wire or a bad thermostat of a zone valve that is stuck open and wont close.
|
|
|
|  |
|