Replacing a Generic Digital Lux with the above programable. On the Lux the following wires were connected: White Wire to W Red Wire to RH Jumper to RC Blue Wire to B Brown Wire to O Yellow Wire to Y Green Wire to G This is a conventional FHA & Cooling System
On the RTH7500 I have RC, R, W, Y, G, C, Y2, W2 My confusion is the wire that were on the Lux B & O Terminals Any help would be appreciated
Thanks
Rich T.
| | Replies:
|
| dac122 | "Re(1):Bought a Honeywell RTH7500 Thermo" , posted Thu 6 Nov 09:02  
If you can wire your Lux back up, probe it with a voltmeter, and then run your system in cool and heat, it should be possible to determine which is your reversing valve. Note that some systems have lock out for up to 5 minutes when going between heat and cool, so wait a while when running those two cases.
|
| Houston204 
| "Re(1):Bought a Honeywell RTH7500 Thermo" , posted Wed 5 Nov 18:49  
Looks like a heat pump stat to me. Do you have the old stat's model number? What brand is your outdoor unit?
The Honeywell RTH7500 requires that you choose either O or B for the reversing valve. If you were using both for a damper system or ambient control, you will need a different stat.
It is slightly possible that B was common. I doubt this though, I haven't seen Lux identify common as B before. Trane does.
White Rodgers has some good choices.