| Markwi | "Furnace Shutting Off." , posted Mon 10 Nov 18:51  
Hello, I have a Miller M3RL060ABW furnace which we got back in 2004 it worked great for the first year. When we turn it on it will blow heat out and then it's the blower I think that will trip out and then it only blows out cold air it will do this until I hit the reset switch. It does it often and I'm not sure what the cause is. It seems that it won't shut off the blower at night time only.
Here are few images of my furnace
Main http://realunsociable.com/furn/DSC00815.JPG
Part that I have to reset the switch, the yellow box is were I press to reset.
http://realunsociable.com/furn/DSC00819.JPG
Here is my thermostat
http://realunsociable.com/furn/DSC00823.JPG
It's set to heat and fan automatic.
Thanks, Mark
| | Replies:
|
| holderlehvac | "Re(1):Furnace Shutting Off." , posted Mon 10 Nov 20:53  
Inducer high temp switch, check for a restricted flue not limited to anything in the pipe from a tennis ball to toys, bees nest ect
Power is using mind over matter
|
| holderlehvac | "Re(1):Furnace Shutting Off." , posted Mon 10 Nov 20:51  
Thats high temp sitch for inducer assembly , a restricted flue is where to start checking for the problem.
Power is using mind over matter
|
|
|
|  |
|