| darrell3612 | "Burners not igniting" , posted Mon 10 Nov 19:48:  
I just noticed that my furnace isn't coming on. I recently noticed a temp drop in the house, and when I checked the furnace to see how it was cycling, I noticed that the inducer fac is coming on, a few seconds later, I hear a click when the HSI lights up, and roughly 10-15 seconds later, I hear another click, as if the gas valve is opening, but the burners don't ignite. However, I did check for the smell of gas, and I don't smell gas after the click when the gas valve opens. After the furnace went through it's cycle a few times, it shut down, and a red light is blinking, four times, and based on the diagnostics, four times indicates a possible ignition problem, and there's notes to check the grounding. Any help would be greatly appreciated.
FYI....I have a Tappan furnace
Darrell demckinneyjr1@yahoo.com
[this message was edited by darrell3612 on Mon 10 Nov 19:53] | | Replies:
|
| holderlehvac | "Re(1):Burners not igniting" , posted Mon 10 Nov 20:46  
I would slowly losen the drip leg on gas line and make sure you have gas there. next step is to check the outlet pressure tap off the gas valve. Unless you have the proper equiptment i would NOT procede further, contact a local service provider.