| royto | "No Heat" , posted Tue 11 Nov 10:17  
Goodman gmpn060-3. Heat was running until yesterday. Went through the unit instruction to restart, no dice.
When calling from the t-stat, it cycles normally, hot surface ignitor glows, but the flame never starts. It will cycle a couple more times, but still nothing.
LED is red the entire time.
royto
| | Replies:
|
| Jojo98 | "Re(1):No Heat" , posted Tue 11 Nov 11:57  
Read Gallatin's post, and do what he suggests in the last sentance
|
| GallatinAC | "Re(1):No Heat" , posted Tue 11 Nov 10:51  
Check gas supply. Check control voltage to gas valve. If gas ok, and no call to the gas valve when the ignitor is glowing, then you may have a safty tripped. Call a tech.
Gallatinac.com
|
|
|
|