Trane airhandler - http://www.hvacmechanic.com/ Forums


Original message

jddesantis

72.145.194.138

"Trane airhandler" , posted Sat 26 Aug 10:29:user profileedit/delete messagepost reply


Yes I am having problem with a trane upflow twg025a140a airhandler it has a slab coil inside of it.the problem is the water is falling off the coil fins before it reaches to its drain pan I have cleaned the coil which was'nt dirty also the drain.This unit is 5 years old.
I don't know what else to do.

[this message was edited by jddesantis on Sat 26 Aug 10:30]

 

Replies:

lee12

66.192.138.173

"Re(1):Trane airhandler" , posted Wed 23 Jan 09:53user profileedit/delete messagepost reply


ddc66 is probably correct, but i've seen this problem before as well. if the static pressure is right, i have seen where the superheat of the coil is not correct(basically has a warm spot) which causes the water to drip off the coil before it has a chance to make it to the drain pan. just a thought. good luck!

 

tofersac



97.97.29.26

"Re(1):Trane airhandler" , posted Sun 7 Oct 14:11user profileedit/delete messagepost reply


ddc66 is right... try making return bigger,sounds like it would be airflow problems.if problem continues, install baffle kit.
good luck

BE HAPPY !!!!!!!

 

chandler57

24.38.132.38

"Re(1):Trane airhandler" , posted Thu 16 Aug 11:38user profileedit/delete messagepost reply


If this problem just occured, check the condensate drain line for a plugged vent or no vent at all. Clean the condensate drain and make sure water drains away. Make sure air filter is clean. If this happens every year, you may need to lower blower speed.

If they don't find ya handsome nor handy surgery may help!

 

trouble

24.113.22.159

"Re(1):Trane airhandler" , posted Fri 10 Aug 09:45user profileedit/delete messagepost reply


Trane has (had) a problem with tvf030 model slab coils, yes they have a baffle kit that is a manufactored complexity to install, it's almost easier to install a A frame Mortex coil(bonus, includes a TXV), The coil will fit (rotated 90 degrees) on the 1/2" split between air handler and coil compartment, if you are clever the existing entry holes for gas and liquid lines can be used, cond. exits through new hole bored on right or left side of furnace (2 hour job)

trouble

 

tommiegeary

24.196.162.60

"Re(1):Trane airhandler" , posted Thu 28 Sep 23:19user profileedit/delete messagepost reply


mix liquid cascade with water and spray coil

Nona?

 

btupro

216.54.60.249

"Re(1):Trane airhandler" , posted Fri 8 Sep 12:41user profileedit/delete messagepost reply


There is a baffle kit that can be purchased for this unit that will redirect the water. This unit is designed for upflow and discharge left (only)and thats why they use a slab coil on this air handler.

Greg Cabe
field service rep.

 

ddc66

205.188.116.139

"Re(1):Trane airhandler" , posted Mon 4 Sep 21:01user profileedit/delete messagepost reply


i have run into this problem on other units where there wasnt enough return air and the negative pressure was nopt allowing the condensation to drain properly. so you may want to check for adequate return air

 

usmcmeyers

64.136.27.229

"Re(1):Trane airhandler" , posted Fri 1 Sep 23:53user profileedit/delete messagepost reply


I installed a Trane upflow air handler with a slab coil today. Are you sure that your unit isn't sweating too bad. Also check your drain pan for leaks. I may be making it to the drain pan but if the drain pan is cracked...check it out.

 

BassetHeating



70.56.246.101

"Re(1):Trane airhandler" , posted Fri 1 Sep 06:43user profileedit/delete messagepost reply


Did I read this correctly? You have an upflow airhandler with a slab coil? If this is the case, therein lies the problem.

Mike

 

 

kenshvac

68.115.180.183

"Re(2):Trane airhandler" , posted Mon 26 Nov 18:46user profileedit/delete messagepost reply


quote:
Did I read this correctly? You have an upflow airhandler with a slab coil? If this is the case, therein lies the problem. ...
exactly what i was thinking.good call

restoring comfort daily

 

 

Zzz

205.250.200.46

"Re(2):Trane airhandler" , posted Sun 12 Nov 10:09user profileedit/delete messagepost reply


Slab coils are famous for this, the problem is they are not well designed for this application and the air flow throws the water right off the coil, you might try slowing the blower down but I'd be looking more towards replacing the coil with an a-coil.