Need help on venting out a dumpster room and how much CFM

PostPosted: Sun May 27, 2012 5:53 pm
by jamit
Hi everyone. I have a question I have a room that is 36'x13' and 15' walls the room is for a garbage compactor . On the south wall has a 16"x16" louver on the left and the right side is a 16"x16" SX095RC Penn inline ventilator rated at about max 849 CFM in a 17' duct The issue I have is the smell is real bad and dont seem the smell is being vented out The louver all the way open and the inline fan is set at high. What do I need to do to get the smell out? anything would be helpful like air flow anything would help Thanks

- Need help on venting out a dumpster room and how much CF

PostPosted: Wed May 30, 2012 3:21 pm
by Freon
If the exhaust fan and the replenishing air inflow are both located on the same wall (south), you may not be getting any flow of air across the compactor.You need the exhaust on one side of the compactor and the supply air on the other so air flows across the compactor.

- Need help on venting out a dumpster room and how much CF

PostPosted: Thu May 31, 2012 12:29 am
by jamit
Thanks for the reply the other issue I have is that the south wall is my only outside wall to outsideand the only wall to have a fan on. The inline fan has a 17' duct that goes to the end of the compactor. Two days ago I closed the fresh air damper all the way and it helped a little.

- Need help on venting out a dumpster room and how much CF

PostPosted: Thu May 31, 2012 7:36 pm
by Freon
Run a duct from the south wall to the north wall for return air (air into the room). Use large ducting if it's a long way and metal. The more air in, the more stink out. You need flow across the dumpster.

- Need help on venting out a dumpster room and how much CF

PostPosted: Fri Jun 08, 2012 11:31 pm
by jamit
How much CFM do I need ? because the negitve air needs to be sucked ?

- Need help on venting out a dumpster room and how much CF

PostPosted: Mon Jun 11, 2012 3:20 pm
by Freon
Go buy an off-the-shelf kitchen vent fan as big as they make. You will probably run this fan 24/7. That will determine the cfm you will need for the air supply (air into the room). Based on the cfm we can tell you the diameter of the duct you will need to run from the south wall to supply the air to the room. Bigger ducting is always better and necessary if there are too many 90 degree elbows. If you need to make a 90 degree turn, use 2@45 degrees... less friction.