carrier pav 111/13120 upflow furnace code 31

General topics about all things heating, ventilation, air conditioning and refrigeration.

carrier pav 111/13120 upflow furnace code 31

Postby dkay1111 » Tue Jan 29, 2013 3:13 pm

I am getting code 31 on our carrier furnace- reset dss and main blower comes on but no heat- inducer motor turns freely but does not run -thanks in advance DK
dkay1111
New Contributor
 
Posts: 5
Joined: Tue Jan 29, 2013 3:08 pm

- carrier pav * upflow furnace code 31

Postby Freon » Tue Jan 29, 2013 5:24 pm

Please post the model number again. Do not use and dashes or slashes or question marks as they get deleted. Turn off the power to the furnace for 10 minutes to reset the control board. Have someone at the thermostat call for heat while you are at the furnace observing closely. Please describe exactly what happens and when. Use paper and pencil. The more details the better the chances of finding the problem.
Freon
Most Valued Contributor
 
Posts: 992
Joined: Sat Jun 18, 2011 11:26 am

- carrier pav * upflow furnace code 31

Postby dkay1111 » Tue Jan 29, 2013 7:54 pm

it a carrier 58 PAV 111 / 13120 upflow- how do you reset the control board as I see no reset botton - thanks in advance DK
dkay1111
New Contributor
 
Posts: 5
Joined: Tue Jan 29, 2013 3:08 pm

- carrier pav * upflow furnace code 31

Postby Freon » Wed Jan 30, 2013 12:18 pm

Your error code involves the inducer assembly. If the inducer motor is not turning on then that is the problem. Either it is not getting power from the control board or the motor itself is bad. To reset the control board, turn off the power to the furnace for about 10 minutes. Without the inducer starting immediately when you call for heat, the furnace isn't going to run.
Freon
Most Valued Contributor
 
Posts: 992
Joined: Sat Jun 18, 2011 11:26 am

- carrier pav * upflow furnace code 31

Postby dkay1111 » Wed Jan 30, 2013 2:42 pm

is there a way to test the inducer draft * there is a test lug on the control board- how would I do that? thanks in advance
dkay1111
New Contributor
 
Posts: 5
Joined: Tue Jan 29, 2013 3:08 pm

- carrier pav * upflow furnace code 31

Postby Freon » Wed Jan 30, 2013 2:45 pm

There is a board testing procedure but I wouldn't do it unless necessary. You may fry the board by accident. The easy way to test the inducer power is remove the inducer motor plug from the control board and then have someone call for heat and you measure the AC voltage at the control board terminals where the inducer motor connects. You should measure 120 volts AC.
Freon
Most Valued Contributor
 
Posts: 992
Joined: Sat Jun 18, 2011 11:26 am

- carrier pav * upflow furnace code 31

Postby dkay1111 » Wed Jan 30, 2013 4:53 pm

I took an extention cord and ran the inducer - it runs fine (Quiet /fast) then I plugged droplight in at control board- there is no power coming out of it- is it the control board? or is there something else I should check- thanks
dkay1111
New Contributor
 
Posts: 5
Joined: Tue Jan 29, 2013 3:08 pm

- carrier pav * upflow furnace code 31

Postby dkay1111 » Wed Jan 30, 2013 4:54 pm

keeps putting * in place of words--- no power at lug on control board that goes to draft inducer
dkay1111
New Contributor
 
Posts: 5
Joined: Tue Jan 29, 2013 3:08 pm

- carrier pav * upflow furnace code 31

Postby Freon » Thu Jan 31, 2013 12:02 pm

If the inducer motor runs when you directly power it AND If there is no power at the control board plug for the inducer motor, you have found your problem. You might inspect the control board closely for loose solder joints especially near the plug for the inducer connection. Usually there will be a small relay that is energized by the digital circuitry and switches the 120 volts AC to the inducer plug. Possibly that is the problem. You might start looking for a new control board.