Honeywell Stat

PostPosted: Thu Feb 06, 2014 3:48 pm
by wildwood
I have a Honeywell (mod #8321U1006) I have the installer 380 set to 1 and it will not work. The Stat is set to 40% humidify and reads 70%, and the AC will not start, the original worked just fine.
I bought this Stat in 2007 and it died in 2013 out of warranty. I bought a replacement and it dos not work, , I sent it back and they sent me another one (TH8321U1006) and that one dose not work either, 2 Stats cant be bad with the same problem, what am I doing wrong ????????
I would need some HELP

THANK'S

- Honeywell Stat

PostPosted: Fri Feb 07, 2014 12:08 pm
by Freon
How is the thermostat powered? Are you connecting the Common and using the 24 volts AC for power or only the battery?

- Honeywell Stat

PostPosted: Fri Feb 07, 2014 7:15 pm
by wildwood
It is powered by C and Battery back up.

- Honeywell Stat

PostPosted: Fri Feb 07, 2014 7:17 pm
by wildwood
Common and using the 24 volts AC for power

- Honeywell Stat

PostPosted: Sat Feb 08, 2014 2:39 pm
by Freon
If you manually lower the temp below the house temp does the AC come on? Do you notice the relative humidity that's displayed changing?