Gas furnace problem

General topics about all things heating, ventilation, air conditioning and refrigeration.

Gas furnace problem

Postby brentj » Thu Jan 27, 2011 10:35 am

I have a Lennox furnace model GS11Q4E100-5NLT that started giving me problems. It was working fine but then it started short cycling on the heat cycle. What I mean is that if you set the heat to 70 degrees and say it was 65 in the house it would come on and run for a couple of minutes and then cut off before reaching the set temp. Finally it stopped working all together. I do know that this unit has the intermittent pilot so I had some help checking it and when you work the thermostat to call for heat the pilot lights. So I thought that the flame sensor had gone out. I replaced the sensor last night and am still not getting heat. I do not know where to go next with this. If I havent supplied enough information then let me know what else you need and I will get that on here.

Thanks
brentj
Minimal
 
Posts: 1
Joined: Thu Jan 27, 2011 10:24 am

- Gas furnace problem

Postby nomadpeo » Sat Jan 29, 2011 11:02 am

also, is your thermostat digital or mechanical.
nomadpeo
Most Valued Contributor
 
Posts: 278
Joined: Wed Jan 12, 2011 10:10 pm

- Gas furnace problem

Postby 4ftBanger » Sat Jan 29, 2011 12:45 pm

It sounds like the ignition controls and components are working. If it were a flame sensor the burners would only stay lit for a few seconds (typically around 7) Based on your description I would suspect either a thermostat problem, or more likely a defective temperature limit in the furnace.
4ftBanger
Most Valued Contributor
 
Posts: 64
Joined: Sat Jan 29, 2011 12:31 pm
Location: Virginia Beach, VA

- Gas furnace problem

Postby nomadpeo » Sun Jan 30, 2011 9:18 am

if it is the limit, it may be doing its job when it sees too much heat buildup. this can happen if all the vents are not open or if the evaporator or filter are restricted.

if you have a mechanical thermostat, the heat anticipator could be set wrong. it is probably an airflow issue.
nomadpeo
Most Valued Contributor
 
Posts: 278
Joined: Wed Jan 12, 2011 10:10 pm

- Gas furnace problem

Postby nomadpeo » Mon Jan 31, 2011 7:50 am

agree with dilkey. measure temp of air in and out and compare against temp rise rating on nameplate. if too high, air is moving too slowly through the heat exchanger due to restriction and opening a limit switch.
nomadpeo
Most Valued Contributor
 
Posts: 278
Joined: Wed Jan 12, 2011 10:10 pm