How to test a thermostat with a multi meter

General topics about all things heating, ventilation, air conditioning and refrigeration.

Moderator: juster

Post Reply
kajaydA
Minimal
Posts: 1
Joined: Sun Feb 06, 2011 10:34 am

How to test a thermostat with a multi meter

Post by kajaydA » Sun Feb 06, 2011 11:00 am

I would like to know how to test a digital thermostat (new Honeywell programmable) with a multimeter at the furnace control board The control board is Honeywell TotalZone.

I have standard mult-meter and need to know where to put the leads and what settings. Also, is this signal in millivolts DC and what range?

So, when the thermostat should be calling for heat, what should the multi-meter read at the control board?

Thanks in advance,

Jay

4ftBanger
Most Valued Contributor
Posts: 64
Joined: Sat Jan 29, 2011 11:31 am
Location: Virginia Beach, VA

- How to test a thermostat with a multi meter

Post by 4ftBanger » Sun Feb 06, 2011 11:15 am

Almost all conventional heating & cooling systems use a 24 volt AC control signal and most use a standard wiring (that is, the wiring terminals are typically marked R, W, Y, G and C).

There are points of high voltage on the board so if you aren't comfortable working with electricity.....
DO NOT ATTEMPT TO DO THIS YOURSELF.

At the furnace control there should be approximately 24 volts measured between the R terminal and the C terminal. During a call for heat on a gas furnace there should be 24 volts between the W terminal and C terminal.
Matt R -
Factory Service Rep for Daikin, LG, Seresco, Climatemaster & Emerson