Gas furnace question

Post by dt67467 » Wed Feb 09, 2011 1:58 pm

The air from my gas furnace starts out hot and cools to nearly room temp as the unit runs. This causes it to run for hours with no progress in warming the room. If i shut it off for 10 - 15 minutes and turn it back on, it starts out hot again, but the end result is the same. Any help? Thanks

4ftBanger
Most Valued Contributor
Posts: 64
Joined: Sat Jan 29, 2011 11:31 am
Location: Virginia Beach, VA

- Gas furnace question

Post by 4ftBanger » Wed Feb 09, 2011 2:53 pm

Two things to check -

1st - Are the burners staying lit through the cycle. If they are not staying lit then you likely have an airflow condition causing a heat exchanger overheating situation or a faulty temperature limit switch.

2nd - Check your ductwork. Even a small leak in the return air ducting, especially in an unconditioned space like an attic, can cause the relative supply temperature to be a lot lower than normal.
Matt R -
Factory Service Rep for Daikin, LG, Seresco, Climatemaster & Emerson