inducer blower cycling off and on

Problems related to residential installations.

inducer blower cycling off and on

Postby TwistedInc » Sun Oct 16, 2011 12:38 pm

i have a Tempstar DC90 that the inducer motor will continually cycle after the furnace reaches t-stat set point and the main blower shuts down, I replaced the t-stat with a new one and still didnt correct the problem. the furnace does not try to light during this time and when the t-stat calls for heat everything works normal. Any advice on where to look *
TwistedInc
Minimal
 
Posts: 1
Joined: Sun Oct 16, 2011 12:27 pm

- inducer blower cycling off and on

Postby Freon » Thu Oct 20, 2011 2:52 pm

The inducer should only run when there is a call for heat. Since the furnace shuts off correctly when the set temp is reached, I will assume the call for heat is also off. But to be sure, find the with from that connects to the W terminal (heat) and disconnect it (TURN OFF POWER while doing this). Set the thermostat so there is no call for heat. Now if the inducer cycles when you turn on power to the furnace then I would say your control board is flaky. If the inducer does not behave abnormally (no cycling), then investigate the thermostat. With the W wire still disconnected at the furnace, check the voltage (carefully) at the W terminal at the thermostat (between W and Common). Since you are not calling for heat, there should be 0 volts AC. If you see intermittent voltages, your thermostat may be flaky.
Freon
Most Valued Contributor
 
Posts: 577
Joined: Sat Jun 18, 2011 11:26 am


Return to Residential