Vent damper wont open

Problems related to residential installations.

- Vent damper wont open

Postby Freon » Tue Nov 01, 2011 3:11 pm

I would disconnect all power to the boiler and wait 30 minutes then turn power back on. Hopefully that may reset the control board and get the damper solenoid working again.

If that doesn't work you need to verify that the damper itself is free to open and close and also that there is voltage at the damper solenoid when you call for heat. BE CAREFUL. I do not know if that damper is 120 volts AC or 25 volts AC. With a voltmeter measure between the two leads to the solenoid on a 120 volt scale. Even if it's 25 volts, you'll see a needle deflection telling you power is there. If you have power then I would suspect the solenoid. If you don't have power, I'd suspect the control board.

To test the solenoid itself, turn off power to the boiler, disconnect the wires to the solenoid and then measure impedance (continuity) at the solenoid itself. If there is no continuity (open circuit), the solenoid is bad.
Freon
Most Valued Contributor
 
Posts: 693
Joined: Sat Jun 18, 2011 11:26 am

- Vent damper wont open

Postby Freon » Thu Nov 03, 2011 2:22 pm

Can you describe the wiring from the damper? There should be 2 wires that power the solenoid to open the damper and then one or 2 wires to show the damper is open (proof of nominal operation) Or the power to the solenoid is in series with the proof switch and there will be only 2 wires. I am guessing at this. Maybe the damper has a model number. But 2 things need to happen... the damper has to open (solenoid works) and the damper tells the control board, we're open, start ignition. The second part is usually a simple switch that will close when the damper opens completing the series safety circuit. Again I am speculating so any information will help. Try and find manuals.
Freon
Most Valued Contributor
 
Posts: 693
Joined: Sat Jun 18, 2011 11:26 am