Rheem Criterion II Won't Ignite Gas

Problems related to residential installations.

- Rheem Criterion II Won't Ignite Gas

Postby Silverjwj » Sun Oct 28, 2012 11:58 am

Check for good ground? Sounds like a similar issue a tech friend of my went thru and I think it was a ground issue.
Silverjwj
Regular Contributor
 
Posts: 21
Joined: Mon Dec 12, 2011 8:36 pm

- Rheem Criterion II Won't Ignite Gas

Postby Freon » Mon Oct 29, 2012 8:30 am

" Blower comes on, cycles through, and releases gas but the igniter never glows"

This observation indicates the pressure switch is working fine. If it were not you would never have gas flowing.

"Disconnecting the connector to the pressure switch and checking the voltage at the connector it remains at a steady 24VAC"

Does the above happen with the gas flowing too?

I would double check your AC voltage measurements. If you look on the control board you should find a small relay that's used to power the HSI. Possibly that relay is the problem. Check the board for any signs of loose connections/cold solder joints. You can always jumper the pressure switch connector to totally remove the switch from the circuit but I doubt it's the switch... they work or they don't.

Another possibility is the gas valve solenoid, when activated opening the gas valve, is causing the voltage drop. You can measure the impedance of the solenoid coil and see if it's correct. Also check the transformer connections to the control board.
Freon
Most Valued Contributor
 
Posts: 578
Joined: Sat Jun 18, 2011 11:26 am

- Rheem Criterion II Won't Ignite Gas

Postby Freon » Tue Oct 30, 2012 1:49 pm

That Siemens device may be the relay. There should be 2 traces to the coil side (24 volts) and 2 leads on the switch side (120 volts) going to the HSI. Check the traces on the 120 volt side for cold solder joints/loose connection. Check the socket and connector. Check for 120 volts on the load side of the relay.

Find where the 24 volt AC transformer is located and while calling for heat measure the voltage on the 24 volt side of the transformer making sure it stays constant at around 24 volts AC. We'll work our way to the HSI making sure we don't miss the real problem by jumping ahead. But since you originally said the gas flows but doesn't ignite, due to the HSI malfunctioning, it does seem the HSI circuit is the problem.

If you can be sure it is a relay problem and can find it online, replacing it is easy if you're handy with a soldering iron.
Freon
Most Valued Contributor
 
Posts: 578
Joined: Sat Jun 18, 2011 11:26 am