gas to LP questions

Problems related to residential installations.

Moderator: juster

Post Reply
jamit
New Contributor
Posts: 6
Joined: Sun May 27, 2012 5:20 pm

gas to LP questions

Post by jamit » Sat Dec 01, 2012 1:25 pm

Hi my first question is which size of orifices to use their is a 1.30mm 1.25mm 1.20mm * And my last question is how do you set the propane * I dont own a manometer * Thanks

ServiceManager
New Contributor
Posts: 6
Joined: Sun Apr 14, 2013 1:35 pm
Location: Valdosta, Ga.
Contact:

- gas to LP questions

Post by ServiceManager » Sun Apr 14, 2013 2:41 pm

jamit -
> Hi my first question is which size of orifices to use their is a 1.30mm
> 1.25mm 1.20mm * And my last question is how do you set the propane * I dont
> own a manometer * Thanks


Most LP Kits come with one set of orifices, Nat Gas will be much bigger then LP orifices will be "as far as the hole sizes" I would use the 1.25mm or 1.20mm.

Kit should also has a spring that you will need to replace inside the gas valve then you will need a manometer to be sure you're gas pressure is set right. Trust me that is a step you do not want to blow off. I hope this helps

Post Reply