Good Morning all,
I have a Honeywell SV9540 Gas Valve with the ST9160 Electronic Fan Timer. The T-Stat tells commands heat, I hear one realy click on the ST9160 and that is all. The start up fan does not come on and the ign. stays off, and I have a steady blinking light.
I do have 24VAC at the SV9540 on/off switch.
The AC Works
The Fan Works
The Fuse is good.
-
1. How can I prove all my safety switches are ** (open or short)
2. Is there suppose to be any voltage going to the relay (black and white wire) on the SV9540 when the t-stat has heat * (I have zero volts all the time, I believe this is my problem)
3. I checked all heat switches and they all read zero ohms (short) which is good.
Any and all information to help prove or dis-prove the GAS valve will be Greatly appreciated.
Thanks in Advance,
B