Furnace blower won't run with Fan only setting on thermostat

Problems related to residential installations.

- Furnace blower won't run with Fan only setting on thermo

Postby Freon » Sun Feb 03, 2013 4:35 pm

You are correct, the common is the neutral.

Not knowing that control I can not say for certain what M1 and M2 are. However if there is also a Cool and Heat spade connection with the other 2 motor wires attached, then I think your assumption about M1 and M2 as being the same as Park is correct. You can move either wire from the M spade to the Fan spade. The only difference between the wires is the motor speed you'll have.
Freon
Most Valued Contributor
 
Posts: 681
Joined: Sat Jun 18, 2011 11:26 am

- Furnace blower won't run with Fan only setting on thermo

Postby Jrossi266 » Sun Feb 03, 2013 5:10 pm

Worked. thanks so much!
Jrossi266
New Contributor
 
Posts: 7
Joined: Sat Jan 26, 2013 3:08 pm

- Furnace blower won't run with Fan only setting on thermo

Postby Freon » Sun Feb 03, 2013 6:02 pm

Enjoy your air flow.
Freon
Most Valued Contributor
 
Posts: 681
Joined: Sat Jun 18, 2011 11:26 am