trane fan issue

Problems related to residential installations.

trane fan issue

Postby gasmann2000 » Mon Oct 28, 2013 7:51 pm

i have a trane model tdd080c936c3. The main board was replaced and now the heat does not work and the fan runs continuously. the board blinks 5 times which says flame roll out detected. I checked all the switches and they check out fine. Im at a loss. please help. ty
gasmann2000
Minimal
 
Posts: 1
Joined: Sun Oct 27, 2013 8:05 pm

- trane fan issue

Postby Freon » Tue Oct 29, 2013 3:22 pm

Did you contact whomever replaced the main board? Was the power to the furnace turned off when the board was replaced? Why was the board replaced? Did the furnace every work properly with the new board?

Jumper the roll-out switche(s) TEMPORARILY (observing the flame as the furnace starts). If you still have the issues then I think the board is bad. If you turn off power to the furnace for 15 minutes you should reset the board and the fan should stop. If the fan does not stop, another bad board indication. Double check that the thermostat isn't set to FAN-ON.
Freon
Most Valued Contributor
 
Posts: 691
Joined: Sat Jun 18, 2011 11:26 am


Return to Residential