goodman electric heat furnace mod #aruf036-00a-1a

Post by heatseeker » Wed Jul 06, 2011 9:23 am

Have problem with unit fan will not turn off and one heat strip is activated in cool mode. when t-stat is off blower runs continuously. could problem be the stack relay stuck closed because when I remove 24 volts wire it does not stop the problem.

nomadpeo
Most Valued Contributor
Posts: 278
Joined: Wed Jan 12, 2011 9:10 pm

- goodman electric heat furnace mod #aruf036-00a-1a

Post by nomadpeo » Wed Jul 06, 2011 2:29 pm

sounds like a stuck switch on the sequencer. if that is the case, you probably have 5kw of heat energized all the time as well.

heatseeker
Most Valued Contributor
Posts: 542
Joined: Wed Jul 06, 2011 9:10 am

- goodman electric heat furnace mod #aruf036-00a-1a

Post by heatseeker » Thu Jul 07, 2011 11:14 am

oh yea Continuos heat, just hard to access sequencers cause installed in front of support beam. replaced heat sequencers and unit working fine. thanks