The outside condensing unit will not run, the fan turns freely and there are no clicks or buzzing coming from the unit...I checked the breaker its ok...I tested the capacitor its ok...Whats next ??? Any and all help greatly appreciated...
Ryd
Minimal
 
Posts: 2
Joined: Tue Aug 09, 2011 1:25 pm

- Goodman Model # GSZ130481AB 4Ton 13Seer HP

Postby heatseeker » Tue Aug 09, 2011 1:43 pm

Sounds like control voltage problem, try to determine if contactor for compressor and fan motor is pulling in if not 24v prob. disconnect the 240 to eliminate the risk of getting shocked before you go stickin your fingers in there.
heatseeker
Most Valued Contributor
 
Posts: 542
Joined: Wed Jul 06, 2011 9:10 am

- Goodman Model # GSZ130481AB 4Ton 13Seer HP

Postby Ryd » Tue Aug 09, 2011 5:53 pm

Thanks heatseeker..... It was the contactor that burnt up.....$14.00 part....I wish all fixes was this cheap