Trane Heat Pump Installation Problems

Problems related to residential installations.

Trane Heat Pump Installation Problems

Postby rbc-tn » Sat Oct 15, 2011 2:38 pm

I had this Trane 16i installed last November. The T-Stat settings were as shown.
After calling them out 2 weeks later a different tech set the T-Stat as shown.
You may see why I have little, to no, confidence in the installer. After
several calls the installer refused to come out again but said my heating bills
where normal for the weather.I went from a 2 ton ~11 sear system to a 16+ sear
2.5/3 ton unit and my electric bill went up over 30%. The AC part of this system
seems to work great and my electric bill fell ~20%. I believe the strip heaters
are coming on whenever the heat comes on. I'm not sure if it's a wiring or
control problem and would like any advice you may want to give. I thought it
would be easiest to check the T-Stat first. Thanks


- 4TWX6036E1000A
Air - 4TEE3F40B1000B
- TCONT803
Trane Cleaneffects


Initial Install
0170 12
0200 1
0210 0
0220 1
0230 1
0260 5
0280 0
0300 1
0310 3
0320 0
0330 2
0350 40
0380 0
0500 0
0510 0
0580 5
0600 90
0610 50
0640 12
0650 0
0660 0
0670 0
0680 2
0690 2
0700 0
0710 0

Corrected Settings
0170 12
0200 0
0220 3
0230 3
0260 9
0270 9
0280 0
0300 1
0310 3
0320 0
0330 2
0340 1
0380 0
0500 0
0510 0
0580 5
0600 90
0610 67
0640 12
0650 0
0660 0
0670 0
0680 2
0690 2
0700 0
0710 0