by nomadpeo » Wed Jun 08, 2011 8:41 am
need to know the setpoint. if it is controlled by pressure, verify cutin and cutout pressures. what are the running pressures and box temp (before extensive ice builds) * what is the box temp near setpoint * is the evap coil clean * are all the fans running * is the condenser coil clean * does it have a solenoid valve on the liquid line * if so, where is it located * what is the sc and sh * inquiring minds would like to know.
you may need to add some more defrost time - maybe every 4 hours. verify defrost heater operation as well. the gasket problem will cause more ice buildup, but an improperly feeding txv can also cause a problem. verify sc and sh.