Furnace just keeps purging

Problems related to residential installations.

Moderator: juster

Post Reply
budwha
Minimal
Posts: 2
Joined: Sat Jan 22, 2011 11:12 am

Furnace just keeps purging

Post by budwha » Sat Jan 22, 2011 11:28 am

I have an older Carrier natural gas furnace( model # 398AAW0360800). When I turn the thermostat to heat the purge fan comes on and the pilot ignites.......thats it...the main valve doesn't seem to come on and it just purges forever. There are no LED lights to help troubleshoot.

erockone
Minimal
Posts: 2
Joined: Sat Jan 22, 2011 5:21 pm

- Furnace just keeps purging

Post by erockone » Sat Jan 22, 2011 5:40 pm

is that a smart valve?

budwha
Minimal
Posts: 2
Joined: Sat Jan 22, 2011 11:12 am

- Furnace just keeps purging

Post by budwha » Sat Jan 22, 2011 9:45 pm

I found the problem....the flame sensor on the pilot light is no good. I temporarily jumped it out and it worked. Will replace the pilot assembly.

Javatango
Minimal
Posts: 1
Joined: Thu Feb 03, 2011 3:17 pm

- Furnace just keeps purging

Post by Javatango » Thu Feb 03, 2011 3:20 pm

I had the same problem with my Lennox gas furnace. Have you tried power cycling the furnace? Power cycling fixed my problem temporarily but I eventually needed to replace the control board.

nomadpeo
Most Valued Contributor
Posts: 278
Joined: Wed Jan 12, 2011 9:10 pm

- Furnace just keeps purging

Post by nomadpeo » Sat Feb 05, 2011 7:28 pm

i was a little puzzled by that statement myself dilkey. if you jumpered out a control with two wires near the burner, it could be a safety device - maybe a rollout sensor. if you do not understand these controls and what they are for, you could be creating a fire hazard. there is nothing there that should be jumpered to allow the furnace to run.