Start up.- suction pressure in cooling on 90 degree day wouldn't go above 70 and head around 300. evap. coil of coarse freezing up, thought it might be expansion valve so we replaced it and that only brought suction up a little, not much. Airflow is fine, removed blower doors and no change in pressures also, fan going right direction, when changing expansion valve blew out lines to see if there was restriction in lines and none were found also no kinks..so I'm out of things, only thing I can think of next would be cap. tubes at evap. coil restricted somewhere..
410a system, If anyone has some sudgestions on what to check, I would be greatfull..
panther
New Contributor
 
Posts: 5
Joined: Sun May 08, 2011 8:53 pm

- ten ton trane split heatpump system 410a freezing issues

Postby panther » Mon May 09, 2011 5:31 am

Really no point in trying to get the superheat and subcool as freezing right away... that's,my thought anyway.
panther
New Contributor
 
Posts: 5
Joined: Sun May 08, 2011 8:53 pm

- ten ton trane split heatpump system 410a freezing issues

Postby panther » Mon May 09, 2011 5:45 am

getting those, will only tell me to add 410 because according to that will show up as low..but adding only raises head to point of going off on head pressue and suction pressure unchanged...
panther
New Contributor
 
Posts: 5
Joined: Sun May 08, 2011 8:53 pm

- ten ton trane split heatpump system 410a freezing issues

Postby stevereno » Mon May 16, 2011 9:43 pm

Agree w/ the Duke...even almost fully restricted cap tubes w/any kind of heat load (latent or sensible), would take time to freeze the system. Airflow.
stevereno
New Contributor
 
Posts: 3
Joined: Sun Jan 16, 2011 3:09 pm
Location: Lexington, KY

- ten ton trane split heatpump system 410a freezing issues

Postby nomadpeo » Thu Jun 09, 2011 8:42 pm

is this a txv cooling coil ? if so, what is the suction pressure when the sub-cooling is in the 7-10 degree range ? properly sub-cooled liquid to the valve should result in reasonable superheat unless the valve is not feeding. if it doesn't feed, suction pressure will be low and superheat high....a matched set. if it is fixed, charging until superheat is reasonable should show up a problem. the high pressure switch on 410 probably won't open until discharge pressure exceeds 600 psig. by the time dp exceeds 400 psig, there should be a clue. we're assuming too non-condensables were properly removed.

as we know, ice will form on the coil below 101 psig suction pressure. seems to me both pressures are low. we don't know for sure there is enough freon. i agree we need to know the numbers. i also agree there could be an airflow issue or equipment match problem assuming standard service procedures were followed. it wouldn't hurt to measure the td across the filter/drier.