Goodman RTU

Postby jtomrai1 » Tue Aug 30, 2011 9:34 pm

I have a Goodman RTU that am having issues with. The model# is weathered completely away. It is an R-22, 5-ton, gas heat. The draft inducer motor is basically short cycling. It turns on for 1-1/2 seconds, then turns off. It is trying to make the circuit, but is failing. I have checked the wiring diagram, everything checks out. I have checked the high limit switch, it's fine. The compressor Model# CRN5-0500-PFV-970. Serial#01H03750B. I have replaced the circuit board because it had 2 burned out resistors. The inducer fan was initially running constantly in heat mode, now it can't make the switch. Any *
jtomrai1
Minimal
 
Posts: 1
Joined: Tue Aug 30, 2011 9:22 pm

- Goodman RTU

Postby heatseeker » Wed Aug 31, 2011 8:48 am

Pressure switch possibly or the motor connections. Wired wrong the compressor has nothing to do with the inducer fan motor. are you running cool when the inducer short cycles or *
heatseeker
Most Valued Contributor
 
Posts: 542
Joined: Wed Jul 06, 2011 9:10 am