Troubleshooting Carrier Furnace on Startup

General topics about all things heating, ventilation, air conditioning and refrigeration.

Troubleshooting Carrier Furnace on Startup

Postby jeffc » Thu Dec 15, 2011 4:07 pm

My Carrier furnace starts up normally (thermostat working, blower on, ignitor glows, flame comes on), but shuts down after about five seconds. Replaced flame sensor with no effect. What other safety mechanism could be causing the gas to shut off after only a few seconds?
jeffc
Minimal
 
Posts: 1
Joined: Thu Dec 15, 2011 4:05 pm

- Troubleshooting Carrier Furnace on Startup

Postby juster » Thu Dec 15, 2011 5:35 pm

lack of proper air flow, did you check your air filter?
juster
Most Valued Contributor
 
Posts: 123
Joined: Tue Mar 30, 2010 7:40 am

- Troubleshooting Carrier Furnace on Startup

Postby heatseeker » Fri Dec 16, 2011 10:17 am

is there a good flame at the sensor?
heatseeker
Most Valued Contributor
 
Posts: 542
Joined: Wed Jul 06, 2011 9:10 am

- Troubleshooting Carrier Furnace on Startup

Postby Freon » Sat Dec 17, 2011 12:08 pm

Shutting down so quickly could indicate either a flame sensing issue or a draft inducer pressure issue. If you can follow theduke03's recommendations you may have less testing to do. But since you replaced the flame sensor you could try TEMPORARILY jumping the pressure switch on the inducer blower. If that stops the problem, then check the flue for any type of blockage.

Lastly, if the inducer and flame sensor are good (new), then I would suspect the control board, especially if it's positioned close to the firebox (excessive heat kills electronics).