not cooling

Problems related to residential installations.

Moderator: juster

Post Reply
Dxrocaa4
New Contributor
Posts: 9
Joined: Fri Apr 06, 2012 3:44 pm

not cooling

Post by Dxrocaa4 » Tue May 01, 2012 2:34 pm

I'm fairly new to HVAC----In the few months I've been doing this never had a big issue with a unit like i"m dealing with now----When call for cooling only get room temp air----this is a split system ---gas furnace works fine---but not the AC---blowers inside & out work---changed filters---cleaned coils---refrig level is great---Am I missing something?

Dxrocaa4
New Contributor
Posts: 9
Joined: Fri Apr 06, 2012 3:44 pm

- not cooling

Post by Dxrocaa4 » Tue May 01, 2012 6:20 pm

Super heat is 14 calls for 12 ---it is with range. Right?

heatseeker
Most Valued Contributor
Posts: 542
Joined: Wed Jul 06, 2011 9:10 am

- not cooling

Post by heatseeker » Wed May 02, 2012 8:28 am

if the unit is not cooling you definitely missed something. Like the duke said make sure it is the right unit.