Lennox WP18 Humidifier w/ Pro1 IAQ Humidistat

Problems related to residential installations.

Moderator: juster

Post Reply
species8472jj
Minimal
Posts: 2
Joined: Thu Dec 27, 2012 2:52 pm

Lennox WP18 Humidifier w/ Pro1 IAQ Humidistat

Post by species8472jj » Thu Dec 27, 2012 2:54 pm

Furnace - Lennox 2 speed G60
Humidifier - Lennox Healthy Climate WS18
Thermostat/Humidistat - PRO1 IAG T955 WH

I just had the humidifier installed, and the installer also put in a manual humidistat. The humidifier will only activate if there is a call for heat.

My goal is to wire the humidifer to my Thermostat/Humidistat such that when there is a call for humidity, it will activate the furnace blower and activate the humidifier.

So I bought a 24 VAC relay and wired the H and C terminals (of the thermostat) to the "coil" side of the relay. The other 2 terminal of the relay got wired to the humidifier.

When I did this, the furnace blower would turn on when there is a call for humidity, however humidifer fan would not activate.

I had a Honeywell Truesteam humidifer and used the same wiring configuation and it worked fine. I am just not sure why this will not work correctly. I can say that the relay I'm using is brand new and I checked the voltage going into the relay and there is 28 volts going into the relay (according to my volt meter).

Any suggestions would be appreciated.

Freon
Most Valued Contributor
Posts: 1019
Joined: Sat Jun 18, 2011 11:26 am

- Lennox WP18 Humidifier * Pro1 IAQ Humidistat

Post by Freon » Fri Dec 28, 2012 3:29 pm

Is this a simple SPST relay

You say The other 2 terminal of the relay got wired to the humidifier. To what terminals in the humidifier did you wire the relay? Is this a simple 120 volt powering of the humidifier using the relay.

species8472jj
Minimal
Posts: 2
Joined: Thu Dec 27, 2012 2:52 pm

- Lennox WP18 Humidifier * Pro1 IAQ Humidistat

Post by species8472jj » Fri Dec 28, 2012 3:55 pm

Thanks for the reply.

Yes, it is a simple SPST Normally open 24 VAC relay.

The H and C side are attached to the "coil" side. And the two wires from the humidifier are connected to the "normally open" contacts.

I hope this clarifies.

Freon
Most Valued Contributor
Posts: 1019
Joined: Sat Jun 18, 2011 11:26 am

- Lennox WP18 Humidifier * Pro1 IAQ Humidistat

Post by Freon » Sat Dec 29, 2012 1:51 pm

Turn off the power to the furnace. If you take the 2 wires from the humidifier that connect to the relay and twist them together making a connection and then turn on the furnace, does the humidifier run. What is the voltage on these 2 wires going to the humidifier 24 volts or 120 volts.