by Freon » Tue Jan 22, 2013 12:09 pm
I would go to the furnace with a jumper wire. Turn off the power at the usual switch exterior to the furnace. Jumper the R and W terminals thereby calling for heat. Open the blower door. Find the door switch. This is usually a 120 volt main power switch for the furnace. Turn on the power at the exterior switch. Now using the blower door switch, turn on the furnace and watch. If it does not light turn off the power at the door switch and try again. Your goal is to have it light so you can observe exactly how the burners are working. If the ignition is smooth and no odd flame activity then I would focus your energy to the ignitor (HSI) and its effectiveness. Check that the slits at the end are clear since I assume the gas has to enter the HSI tube to be ignited. Watch closely the one burner that is responsible for getting the gas to the HSI and will light first. Usually one burner will lite first and there is a small flame that then lights the other burner.