Slashes, dashes and question marks will generate an *. So avoid those punctuation symbols.
You have the right idea. More air flow through the heat exchanger will drop the temperature. The furnace should be well within the temperature rise if there is the 1200 cfm the high speed is designed to deliver. I have a feeling your duct system is restricting the 1200 cfm air flow. You need to find the return duct(s) diameter as well as all supply ducts. Previously I assumed 6" ducts for the supplies since that's a very common size. Each 6" duct can deliver 110 cfm. You can do the math. Your goal is to get the duct system to handle the 1200 cfm the blower is trying to deliver. Do you have metal ducting or flex. Also, what type filter(s) are you using and what are the dimensions.
If you can find the high limit safety, you may be able to read the temperature at which it opens. Some are stamped on the outside.